Anti-pumping device is a feature incorporated in a Circuit Breaker or reclosing scheme to prevent repeated operation where the closing impulse lasts longer than the sum of the relay and CB operating times. The function of an anti-pumping device is to prevent the circuit breaker closing and opening several times in quick succession. This might be caused by the application of a closing pulse while the circuit breaker is being tripped via the protection relays. Alternatively, it may occur if the circuit breaker is closed on to a fault and the closing pulse is longer than the sum of protection relay and circuit breaker operating times. Circuit breakers with trip free mechanisms do not require this feature.