Home » English riddles » Grounding » Grounding Riddle No.22 – Main Earthing Conductor sizing calculation » Reply To: Grounding Riddle No.22 – Main Earthing Conductor sizing calculation

Reply To: Grounding Riddle No.22 – Main Earthing Conductor sizing calculation

#1858
Hamid

    That mentioned Equation (which was not written correctly) reflect two basic assumptions a) That all heat will be retained in the conductor (adiabatic process). b) That the product of specific heat (SH) and specific weight (SW), TCAP, is approximately constant because SH increases and SW decreases at about the same rate. For most metals, these premises are applicable over a reasonably wide temperature range, as long as the fault duration is within a few seconds. Therefore the thermodynamic behavior of conductors in fault duration ( 1 to 3 sec.) can not affected by conductor thin covering, and you can use submitted constant material values which illustrated in technical tables for required calculations in base of main uncoated conductors. Also about mentioned fault duration (3 sec.), Relay malfunctions can result in fault duration in excess of primary clearing times. The backup clearing time is usually adequate for sizing the conductor. For smaller substations, this may approach 3 s or longer. However, because large substations usually have complex or redundant protection schemes, the fault will generally be cleared in 1 s or less. Meanwhile for correct formula and table you can refer to IEEE 80 or following relations.