Reply To: Protection riddle No.74 – REF Protection on 2MVA Transformer

#2094
Hamid

    REF as one of important unit protection can be applied throughout a power transformer and, since it does not involve time grading, is relatively fast in operation. The speed of response is substantially independent of fault severity. Unit protection usually involves comparison of quantities at the boundaries of the protected zone as defined by the locations of the current transformers. This comparison may be achieved by direct hard-wired connections or may be achieved via a communications link. However certain protection systems derive their ‘restricted’ property from the configuration of the power system and may be classed as unit protection, e.g. earth fault protection applied to the high voltage delta winding of a power transformer. Whichever method is used, it must be kept in mind that selectivity is not merely a matter of relay design. It also depends on the correct coordination of current transformers and relays with a suitable choice of relay settings, taking into account the possible range of such variables as fault currents, maximum load current, system impedances and other related factors, where appropriate. The term