Home » English riddles » Protection » Protection Riddle No.78 – Generation of hidrogen gas in Power Transformer » Reply To: Protection Riddle No.78 – Generation of hidrogen gas in Power Transformer

Reply To: Protection Riddle No.78 – Generation of hidrogen gas in Power Transformer

#2229
bob o

    Hamid, it seems you may have a low level fault. You need to carry out some testing. If you do not want an outage you could try partial discharge testing to see if there is any discharge/ insulation problems within the transformer. What hydrogen levels are in the tapchanger? Is there any gasses building up in the bucholtz? Eventually if the problem persists you will have to have an outage to carry out some testing. Regards