Home » Topics » English riddles » Protection » Protection Riddle No.20 – Single phase earth fault

Protection Riddle No.20 – Single phase earth fault

  • Creator
    Topic
  • #225
    GUEST

      If the star point of a transformer is earthed and one phase develops a fault to earth can anyone provide a link with a detailed explanation to the resultant effect on the healthy phases with respect to earth ?

    Viewing 1 replies (of 1 total)
    • Author
      Replies
    • #1454
      Hamid

        When a phase is grounded, the voltage across this phase will become zero. The other two phasors will remain the same as in a healthy system and add to give the residual voltage. In healthy condition: VR=VA1+VA2+VA0 VY=a2VA1+a VA2+VA0 VB=a VA1+a2VA2+VA0 VA0 =0 (residual voltage) In faulty condition: V’R=0 V’Y=VY+VA0 V’B=VB+VA0 VA0>0