Machine Question No.21 – Output voltage of generator

  • Creator
    Topic
  • #336
    Yogi

      It is well known that, if an Alternator is connected with Grid its (alternator) voltage can not be change and it follows the grid voltage but i've seen that when its excitation changes its voltage also changes, why?
      It is well known that, if an Alternator is connected with Grid its (alternator) voltage can not be change and it follows the grid voltage but i've seen that when its excitation changes its voltage also changes, why?

    Viewing 2 replies - 1 through 2 (of 2 total)
    • Author
      Replies
    • #1640
      Hamid

        It is impossible; the output voltage of generator is fixed by constant voltage of grid indeed they are one voltage that we can measure it in generator output terminals. Of course the internal emf of alternator which you cannot measure it may be changed due to excitation current or load current phase angle variation.

        #2902
        Loveraj suryadev

          Hi yogi, if excitation changes, the magnitude of flux density also changes and we know that generated voltage is directly proportional to the flux density it also changes…. over excited alternator delivers reactive power due to demagnetization effect of armature…. reactive power will be delivered to load and we know that reactive power flows only when their is voltage difference…

        Viewing 2 replies - 1 through 2 (of 2 total)