We are using grounding transformer of following specs
rated voltage 33 kV, connection Zn(zigzag) , fault current/ph -266.7/30s, Zo=52.7ohms/ph Po=1244 W , Io=0.07 A
We are using grounding transformer of following specs
rated voltage 33 kV, connection Zn(zigzag) , fault current/ph -266.7/30s, Zo=52.7ohms/ph Po=1244 W , Io=0.07 AHow can I calculate the positive sequence impedance and the x/r ratios? Is there any data missing to calculate the same?
Viewing 5 replies - 1 through 5 (of 5 total)
Viewing 5 replies - 1 through 5 (of 5 total)
- You must be logged in to reply to this topic.

If three currents, equal in magnitude and phase, are applied to the three terminals, the ampere-turns of the a?-N winding cancel the ampere-turns of the c?- c winding, the ampere-turns of the b?-N winding cancel the ampere turns of the a?-a winding, and the ampere-turns of the c?-N winding cancel the ampere turns of the b?-b winding. Therefore, the transformer allows the three in-phase currents to easily flow to neutral. If three currents, equal in magnitude but 120