Generally the decision about neutral breaking depends on the way of earthing system execution. The neutral must be broken by a multi-pole device: – In TT and TN, if neutral cross-section is less than phase cross-section. – In terminal distribution in view of the Neutral/Phase reversal risk. The neutral must be protected and broken: – In IT for intervention of the protection device on the double fault, with one of the faults possibly on the neutral; – In TT and TN-S if neutral cross-section is less than phase cross-section For all earthing systems if the installation generates harmonic currents of rank 3 and multiples (especially if neutral cross-section is reduced). In TN-C the neutral, which is also the PE, cannot be broken which is dangerous as a result of its potential variations, due to load currents and insulation fault currents. To prevent risks, a local equipotentiality and an earth connection must be provided for each zone/consumer. For details of various earthing system you can refer to IEC 60364 and below figures:
جدیدترین معماها
Recent Topics
معماهای فارسی
- DC سیستم
- الکترومغناطیس
- الکترونیک قدرت
- اندازه گیری الکتریکی
- پرسش های مفهومی
- پست های انتقال و توزیع
- تابلوهای الکتریکی
- ترانسفورماتور
- تست های الکتریکی
- حفاظت الکتریکی
- خطوط انتقال
- سیستم زمین
- سیستم های فشار قوی
- کابل های الکتریکی
- کنترل
- ماشین های الکتریکی
- مباحث عمومی
- مدارهای الکتریکی
- معماهای علمی
- معماهای منطقی
- نیروگاه
