      The Main voltage Transformer associated with the High Voltage system is not provided with a broken delta secondary windings to ….
      The Main voltage Transformer associated with the High Voltage system is not provided with a broken delta secondary windings to polarise the directional Earth fault relay. It is permissible to use three single phase interposing voltage transformers. Why ?

    در حال نمایش 1 پاسخ ( از کل 1)
    • نویسنده
      پاسخ‌ها
    • #3353
      Hamid

        Generally it is possible; you just should care for additional error due to new interface device which is not important in this case.