I was going through 11kV schemes.For every phase R,Y,B there is an individual Potential transformer for the outgoing feeder.
In that I found that the secondary of PT of outgoing feeder is connected in star and the Yellow phase is earthed and not the star point(the neutral). The general philosophy is to earth the star point i.e. the neutral but I wonder why they are earthing the Yellow phase and not the neutral.
در حال نمایش 1 پاسخ ( از کل 1)
در حال نمایش 1 پاسخ ( از کل 1)
- شما برای پاسخ به این موضوع باید وارد شوید.

The three phase, three wire circuit is in common use today for VT circuits in metal clad switchgear. It is common practice to ground one of the phases, usually Y. This arrangement is used when it is desirable to eliminate coordination problems between primary and secondary VT protective devices for phase-to-neutral (ground) short circuits or phase-to- ground insulation failures. Because each mentioned fault in secondary side appears as two phase faults in primary side.