Home » Topics » English riddles » Protection » Protection question No.24 – CT secondary

Protection question No.24 – CT secondary

  • این موضوع 2 پاسخ، 1 کاربر را دارد و آخرین بار در 2 سال، 9 ماه پیش بدست Dinesh Deshmukh به‌روزرسانی شده است.
  • سازنده
    موضوع
  • #249
    bipul pandey

      What happens when ct secondary gets open while selecting through ampere meter selector switch for metering function why dont it get burst/burn when secondary is open momentarally?
      What happens when ct secondary gets open while selecting through ampere meter selector switch for metering function why dont it get burst/burn when secondary is open momentarally?

    در حال نمایش 2 پاسخ ( از کل 2)
    • نویسنده
      پاسخ‌ها
    • #1493
      Hamid

        The changeover switch which used in current transformers circuits shall be “make-before-break” type. This type of switches has a spring loaded action which prevents momentarily circuit disconnection.

        #3017
        Dinesh Deshmukh

          Using Rotary Switch as selector switch,Your CT ckt won’t be open.If switch has go problem ,then CT load is propotional to flux passing through it and hence amount of voltage generated in seondary . IF CT is sparsely loaded ,It takes time and monmentarly opening of CT causes Sound practically and do not bast it:)

        در حال نمایش 2 پاسخ ( از کل 2)
        • شما برای پاسخ به این موضوع باید وارد شوید.