Home » Topics » English riddles » Protection » Protection Question No.40 – Reverse KVAR relay

Protection Question No.40 – Reverse KVAR relay

  • این موضوع 1 پاسخ، 1 کاربر را دارد و آخرین بار در 2 سال، 9 ماه پیش بدست Hamid به‌روزرسانی شده است.
  • سازنده
    موضوع
  • #341
    Ahmed

      Is there reverse KVAR relay similar to reverse power protection relay in power system?
      Is there reverse KVAR relay similar to reverse power protection relay in power system?

    در حال نمایش 1 پاسخ ( از کل 1)
    • نویسنده
      پاسخ‌ها
    • #1647
      Hamid

        In power system, operation in the leading mode (drawing Vars into the generator from the power system) can be required during periods of light load. High-voltage transmission lines are highly capacitive when lightly loaded. The Vars produced by these lines can raise system voltage to unacceptable levels. Under such conditions, generators are operated in the leading mode to absorb excess reactive power, thus controlling system voltage. When a relatively large generator is connected to a weak system, the unit may be required to operate in the leading mode to prevent overvoltage caused by the transmission of real power across the system. The most obvious limit to leading Var operation is the bottom portion of the generator