  • #347
    R K Mohapatra

      Can somebody share the experince of a 100 MVA 220 kV class transforemr working at a continuous oil pressure of 4 kg.
      Can somebody share the experince of a 100 MVA 220 kV class transforemr working at a continuous oil pressure of 4 kg.

    در حال نمایش 2 پاسخ ( از کل 2)
    • نویسنده
      پاسخ‌ها
    • #1108
      Hamid

        Please explain, what do you want to know?

        #1710
        R K Mohapatra

          A very specific requirement calls for pacement of trnasfoirmer at underground while the cooling equipment is at a height of 35 meters above the trnasformer . So , the complete tank and acessories like PRV and OLTC are at a pressure equivalent to 35 meter height of oil column .While we are going ahead with the design of the transformer we expect some problem with the PRV and OLTC ( we prefer vaccum type OLTC )