Home » Topics » English riddles » Protection » Protection Riddle No.76 – Neutral CT rating

Protection Riddle No.76 – Neutral CT rating

  • این موضوع 1 پاسخ، 1 کاربر را دارد و آخرین بار در 2 سال، 9 ماه پیش بدست Hamid به‌روزرسانی شده است.
  • سازنده
    موضوع
  • #562
    Deepa

      Rating of the CT provided in the neutral of the transformer/generator for the earth fault protection is 1/5 of the rated current of the transformer/generator. How this 1/5 is arived? why?
      Rating of the CT provided in the neutral of the transformer/generator for the earth fault protection is 1/5 of the rated current of the transformer/generator. How this 1/5 is arived? why?

    در حال نمایش 1 پاسخ ( از کل 1)
    • نویسنده
      پاسخ‌ها
    • #2130
      Hamid

        According to IEEE 242, when the generator neutral is grounded through an impedance limiting the maximum ground-fault current to a value less than the primary rating of the CTs, a differential ground fault scheme (Device 87G) should be considered. A differential ground-fault scheme, however, is capable of detecting faults to within 10% from the generator neutral. A neutral CT, separate from the ground overcurrent relay CT, may be necessary for maximum relay sensitivity. The ground differential CT should have a primary current rating of 10% to 50% of the neutral resistor-current rating. The neutral-CT-turns ratio and tap setting of the overcurrent relay should be selected to provide an operating current of 5 to 10 times its pickup setting for a bolted line-to-ground fault at the generator line terminals. The pickup setting should be at least equal to and preferably greater than the pickup setting of downstream ground overcurrent devices for selectivity between those relays. The pickup setting should also be set above the anticipated level of any harmonic current flowing in the neutral during normal conditions.

      در حال نمایش 1 پاسخ ( از کل 1)