In an extra high voltage substation, the output overhead lines protected by standard protection system.
That protection system contains high quality main and backup distance protection, sync/auto reclosing relays and separated static relay that specified to line circuit breaker which is named "CBF protection".
The CBF protective relay has connected in series to same current transformer core that connected to distance relay. Also because the extra high voltage power system stability requirements, the relays setting have done in tightly coordination systems. But the designed protection system sometimes couldn't operate correctly.

Sometimes all circuit breakers that connected to one of two substation bus bar (double bus bar system) are tripped due to one sever short circuit that occurred in one of output lines without any bus bar protection activity.
According to more investigation and data recording analyses, the line distance protection had operated correctly (less than 30 ms) and it had opened relevant circuit breaker in time. Also the CBF protective relay had operated too.How can you explain the reason of that protection system mal-operation?
- شما برای پاسخ به این موضوع باید وارد شوید.

CT subsidence current keep the 50BF element asserted longer than necessary and may contribute to a false breaker failure operation in tightly coordinated systems. Nowadays some digital base protective relays are able to detect CT subsidence current.
At Power Plants, the required critical clearing time was calcultated to be 10 cycles. The recommended total clearing time was 9 cycles as shown in Figure below. In order to achieve this total clearing time, it was necessary to purchase a breaker failure relay that had a short fault detector dropout time. The special BF relay is selected because its instruction manual reflected a dropout time of less than 1 ms.