Protection riddle no.6 – Overcurrent protection with two CT

  • این موضوع 1 پاسخ، 1 کاربر را دارد و آخرین بار در 2 سال، 9 ماه پیش بدست Hamid به‌روزرسانی شده است.
  • سازنده
    موضوع
  • #83
    VATKARI from INDIA

      In 3-Phase over current protection scheme sometimes 2 no of Current Transformers used for overcurrent relay activation.

      In 3-Phase over current protection scheme sometimes 2 no of Current Transformers are used for overcurrent relay activation.

      It was observed that one of the secondary terminal of the CTs (input relay) is connected to ground/earthed.

      CAN ANYONE EXPLAIN THE LOGICAL REASONS FOR THIS.

    در حال نمایش 1 پاسخ ( از کل 1)
    • نویسنده
      پاسخ‌ها
    • #1191
      Hamid

        According to standard each secondary circuit of instrument transformers should be a completely self-contained metallic circuit insulated from ground, except at a point in the secondary circuit, to prevent of dangerous touch voltage due to insulation damage or secondary current transformers opening. The grounding should be done at one point, to prevent differences of potential; because of differences of voltage between different points in the station ground grid. Also to facilitate the temporary removal and reestablishment of the ground connection, when desired. The best point in three phase connection is the star point of CTs and relay elements. In 2CTs scheme, this point can not be the star point of relay elements; because in this case one of three elements of relay is bypassed by grounding connections.