Reply To: Protection riddle no.8 – Risk of operation in power plant

#1226
Hamid

    According to general recommendation in network with impedance earthed neutral, if a relay supplied from a ring CT is used, the pick-up may be set at 1.5 times the zero sequence capacitive current of the feeder (of the order of 3 Amps/km for high voltage cables).