Topic
-
According to the contract, we are obliged to provide earth fault protection for an emergency diesel generator. Also, according to the diesel generator manufacturer’s documents, overcurrent and earth fault protection is provided, however, the employer’s consultant claims that the anticipated earth fault protection is not able to protect the earth faults that occur on the generator winding and the earth fault relay must be connected through the allocated neutral ring type current transformer. Given that such a current transformer is not available, is there a solution for this issue?