The inrush current flowing in the primary while energisation of the transformer is not of same magnitude in each phase, they are different in magnitude. Hence there will be phase currents of different magnitude and also it is not balanced through neutral. So there will be differential current in REF relay and hence it may operate during energisation if proper filtering/suppressing of 2nd harmonics is not done.