2021-08-03 at 11:08 am
#2536
Hamid
In first connection, the thermal over load of each individual phase face to 1/3In, therefore the ELCB setting will not correct. In second connection, the balancing of mmf which designed to detection of earth fault is not established in normal loading conditions without any faults; because 3i-i is not zero.