A design query on earthing trafo.
An earthing trafo installed on a 11 kv switchboard is rated for 381 kva , 11 kv/ 110v in a star – broken delta arrangement. A resistor rated 1.14 ohms is connected across the broken limb. …
A design query on earthing trafo.
An earthing trafo installed on a 11 kv switchboard is rated for 381 kva , 11 kv/ 110v in a star – broken delta arrangement. A resistor rated 1.14 ohms is connected across the broken limb.
How can the max earth fault current be calculated using the above data? Can the max earth fault current be assumed to be the full load current of the earthing trafo?
Viewing 5 replies - 1 through 5 (of 5 total)
Viewing 5 replies - 1 through 5 (of 5 total)
- You must be logged in to reply to this topic.

With above connection, the secondary current can be calculated by multiplying the transformer primary current times the transformer ratio. This is the current through the grounding resistor, and its value establishes the continuous current rating of the grounding resistor. The voltage across the resistor under ground-fault conditions is 1.73 times the secondary volltage of the grounding transformer bank (190V for 110V rating). Therefore, I think correct answer is 5 A.