Why the stator winding of the generator cannot be protected 100%. What is the reason? Kindly clarify.
Viewing 1 replies (of 1 total)
Viewing 1 replies (of 1 total)
- You must be logged in to reply to this topic.

If a second ground occurs in the same phase near the generator terminal it will be undetectable and unrestricted by the grounding impedance. The generator differential relay would not operate for this fault, because current at each end of the winding would be the same. This extremely high magnitude fault would persist until it evolved into a phase-to-phase fault that is detectable by the differential relay.
As a result of these considerations and the development of electronic relay technology, several 100% winding protection schemes are now available. They fall into two categories: third-harmonic voltage schemes and neutral injection schemes.