Topic
-
A 20 KV switchgear have equipped with one zig-zag earthing transformer. As you know, A grounding transformer must handle the unbalanced load on the circuit as well as the duty during line-to-ground faults.
If the circuit has a lot of unbalance load, then we must concern the continuous rating of transformer in addition of its short time withstand currents. The continuous rating power of mentioned grounding transformer is 100 KVA.
The primary current setting of related earth fault relay that installed in neutral point of E.T. is 8 Amp.
This set point current is chosen in base of E.T. continuous rating current and following calculations:It =100/ (20×1.73) = 2.89 A
In= 3x It = 8.67 A
But the earth fault current calculation and analyses dictate other primary current setting (12.5 A).
Which one current setting is correct? Which one do you choose?