I was carrying out a fault current distribution for an earthing design for a primary or zone substation when I found the transformer to be used was Yyn0 (33/11 kV). Apparently the lines company here have many substations with these transformers.
I was carrying out a fault current distribution for an earthing design for a primary or zone substation when I found the transformer to be used was Yyn0 (33/11 kV). Apparently the lines company here have many substations with these transformers.When I checked in the books the zero sequence in some books appear like a (i)"floating" impedance (with a value 3 to 10 times the positive impedance) while in other ones (ii) the equivalent circuit appears to be the same as a Dyn transformer.
Most of the books have the equivalent circuit as (i) in which case no zero sequence will flow for a phase to earth fault at the 11 kV feeders. Also when modelling this transformer with the software DigSILENT gives as result a very low value of current for a phase to earth fault.
The question is with this arrangement; Is there any current flowing for a phase to earth fault at the secondary? Having in mind that these substations are located mainly in semi-rural areas with overhead feeders is there any problems with this choice of transformer?
- You must be logged in to reply to this topic.

3-According to above diagram, the Yyn0 connection is provide interconnection path for zero sequence current between two sides of transformer. Therefore each side zero sequence impedance (high impedance probably) can be transfer to opposite side via power transformer and that mentioned software can calculate them. 4- The most common characteristics of three-phase transformer connection grounded wye