Protection Riddle No.18 – Generator Stator Earth-Fault Protection at Low Frequency Injection

  • Creator
    Topic
  • #206
    GUEST

      In Large Generators,for providing 100% Stator Earth Fault protection,low Frequency Injection voltage at 20HZ IS WIDELY USED.

      Why is injected voltage chosen to be 20Hz and not 5Hz or 10 Hz.??

    Viewing 3 replies - 1 through 3 (of 3 total)
    • Author
      Replies
    • #1138
      Hamid

        The relay measurement unit shall be blocked out of 10-40 HZ, because in this frequency range a zero voltage can also be generated by generators starting up or slowing down. The 100-% stator earth fault protection detects earth faults in the stator windings of generators which are connected with the network via a unit transformer. This protection function, which works with an injected 20 Hz voltage, is independent of the system-frequency displacement voltage appearing in earth faults, and detects earth faults in all windings including the machine star point. The measuring principle used is not influenced at all by the generator operating mode and allows to perform measurements even with the generator standing still. The two measuring principles used

        #1630
        Bhupendra Badiya

          20 Hz is totally independent source for fault impedance measurement . 20 Hz is neither harmonic nor subharmonic of 50Hz.

          #1632
          Hamid

            why 20 HZ? Why 10,25,30,40,… HZ cannot be suitable?