In power generation plant with several ungrounded generators and grounding only one generator, how can unearthed generator affecte from network earth faults?
In power generation plant with several ungrounded generators and grounding only one generator, how can unearthed generator affecte from network earth faults?
Viewing 1 replies (of 1 total)
Viewing 1 replies (of 1 total)
- You must be logged in to reply to this topic.

If Zo is less than Z1 or Z2, as is commonly the case, the ground-fault current will be greater than the three-phase fault current Eg/Z1. If several machines are operated in parallel, and only one machine grounded, this effect is accentuated in the grounded machine. When different numbers of machines operating in parallel, with all neutrals ungrounded, and with only one machine grounded which illustrated in Fig. It will be observed that the line-to ground fault current is always greater than the three phase fault current, and that the situation becomes particularly serious as the number of paralleled machines increases. In an installation of this kind, some form of neutral impedance device is a necessity. In order to determine the size of neutral reactor to limit the generator winding current for a single line-to ground fault to the generator winding current on a three phase fault the constants of the generator and the constants of the system must be known. The system constants must include all circuits and sources of supply to the fault except the machine under consideration.