Can a 3500 KVA, 6.3/11 KV power transformer HV side be protected against all faults by installing protection relays only on its primary 6.3 KV side? Overhead line is directly connected at 11 KV side of transformer.
Can a 3500 KVA, 6.3/11 KV power transformer HV side be protected against all faults by installing protection relays only on its primary 6.3 KV side? Overhead line is directly connected at 11 KV side of transformer.Transformer is delta(6.3 KV) – wye ( 11 KV) type with neutral grounded solidly … an idea is to install 51N on neutral of grounded Y at transformer secondary and take its signal to primary side protection relay?
How fault currrents on Y side of transformer reflected on delta side? Can overcurrent relays decide about fault on Y side by sensing current from delta side?
- You must be logged in to reply to this topic.

The variable fault point voltage is also an important factor, as in the case of impedance earthing. For faults close to the neutral end of the winding, the reactance is very low, and results in the highest fault currents. The variation of current with fault position is shown in below Figure.
As you see for faults close to the neutral end of the winding primary the current protection systems cannot have suitable function against secondary fault which can be very sever. Therefore in some case primary side protection cannot cover all secondary fault situations.