Earth fault tripping on starting of Large 3 phase motor. Can current imbalance and CT connection scheme explain this. Or other reason?
Earth fault tripping on starting of Large 3 phase motor. Can current imbalance and CT connection scheme explain this. Or other reason?With 2 different motors we changed the protection settings as recommended (by others) protection study. Earth fault protection on both motors was sensitised to grade with power main switchboard bus bar protection. Now on starting the motors they trip on earth fault.
At starting there is a 4-5% phase current imbalance. Can this explain the earth fault detection due to using a residual connection of the three phase CTs? (Holmgreen connection below) Or is other cause likely?
Motor 1 – 11kV, 3P3W, FLA 243A. Protection relay – GE multilin 269+
Sample log of tripI1= 206A
I2= 202A
I3= 220A
I0= 23.9Anew setting (trips on start) – 0.1xCT Def Time 0.6sec
old setting (okay) – 0.25xCT Def Time 2 secTopicViewing 1 replies (of 1 total)Viewing 1 replies (of 1 total)- You must be logged in to reply to this topic.