Transformer Riddle No.33 – Grounding resistance calculations

  • Creator
    Topic
  • #419
    Hindi

      i want to know how we detrmine (ngr)value in power transformer protection.
      i want to know how we detrmine (ngr)value in power transformer protection,i have a cause in my substation the (ngr) of power transformer 100 MVA 220/33/11 kv y/y/d at 25% loading the load is only in 33kv side 11kv side is not yet used this (ngr) was burend after afault in 33kv feeder which tripped in its time by earth fault relay,iwant to know what cause the (ngr) burend

    Viewing 3 replies - 1 through 3 (of 3 total)
    • Author
      Replies
    • #1773
      Hamid

        Resistance grounding solves the problem of transient over-voltages, thereby reducing equipment damage. Over voltages caused by intermittent (arcing) faults, can be held to phase-to-phase voltage by grounding the system neutral through a resistance which limits the ground current to a value equal to or greater than the capacitive charging current of the system. Thus the fault current can be limited, in order to prevent equipment damage. In addition, limiting fault currents to predetermined maximum values permits the designer to selectively co-ordinate the operation of protective devices, which minimizes system disruption and allows for quick location of the fault. The line-to-ground capacitance associated with system components determines the magnitude of zero-sequence charging current. The resistor must be sized to ensure that the ground fault current limit is greater than the system’s total capacitance-to-ground charging current. If not, then transient over-voltages can occur. The charging current of a system can be calculated by summing the zero-sequence capacitance or determining capacitive reactance of all the cable and equipment connected to the system. For prevention of resistor burning the Rating power of selected NGR shall be considered regarding the time and amount of NGR through earth fault currents. IEEE-32 is the standard used for rating and testing neutral grounding resistors. The most important parameters to consider from IEEE-32 are: the allowable temperature rises of the element for different

        #1777
        hindi

          thank you very much about the information, also i want to add somethnig ,the 33kv feeder which tripped is empty feeder onely charging current with along distance,also the value of the resistance was designed to 50 MVA Y/Y/D transformer which hasd been replaced by 100 MVA transformer after uprating the substation and they didnot change the NGR.

          #1778
          Hamid

            Grounding resistor rating ampere calculation criteria shall be considered base on equipment insulation protection (Ig >3Ic0) for high resistance NGR selection and power system stability (Refer to Machine Riddle No.5) for low impedance NGR selection. But about your problem regarding burning of NGR due to earth fault current, obviously there is not any coordination between your relaying protection system and current time withstand of grounding devices. It seems the specified NGR to previous power transformer was selected regarding power system stability consideration, so in this case, perhaps can be said in rough role: you can select a NGR with rated current two times ( 100MVA/50MVA) of previous NGR current. For time withstand selection of NGR (10sec., 1 min., 10 min.,), I said some selection criteria in above post.