Protection Riddle No.62 – Grounding of primary side of transformers

  • Creator
    Topic
  • #437
    Hamid

      Why the primary side of distribution transformers usually is not grounded?


      Why the primary side of distribution transformers usually is not grounded?

    Viewing 1 replies (of 1 total)
    • Author
      Replies
    • #1810
      Hamid

        The grounding of Primary side of electrical equipments such as distribution/load transformers or electromotor which connected to power sources is not recommanded; because: 1-If the branch breaker trips or opens, a portion of grounding system would be lost, therefore amount of system resistance would be conditional which is not desirable. 2-Relay coordination of system would be difficult. Please note following figure, when an earth fault occur in A point, the earth fault protection of healthy neighbor feeder can be front of maloperation if it is not equipped by directional element.