      Is it possible to power supply of small power electromotor via usual electronic UPS?

      Is it possible to power supply of small power electromotor via usual electronic UPS?

    Viewing 1 replies (of 1 total)
    • Author
      Replies
    • #1883
      Hamid

        The Power Factor, Crest factor and Surge Factor are important and must be considered for sizing UPS systems because of inherent electrical and mechanical structure of electromotor such as starting inrush current and inductive back voltage. Generally most loads of electronic UPS are either inductive or capacitive (e.g. computer and digital systems) and do not utilize all of the current they draw. They have an apparent power rating expressed as Volt-Amps or VA reflecting their total current load and a Wattage rating defining the power they actually consume. The surge factor of a load is the ratio of its startup inrush current to its steady state current demand. For large disk arrays, this can be approximately 1.5, whereas for typical computer systems it is approximately 1.15. UPSs must have sufficient capacity to support the overall surge factor of their driven load. The ratio of apparent to actual power is known as the power factor. Information technology equipment including servers, routers, hubs and storage systems almost always uses power factor corrected power supplies. With a power factor near unity, the difference between their VA and Wattage rating – their reactive power – can be ignored. However many desktop PCs can have a power factor as low as 0.65, which means that their apparent power requirement is 50% higher than the actual power consumed. When sizing UPS systems, therefore, it is essential to specify sufficient capacity in terms of both the wattage power and the current they can deliver. A safety margin can be ensured by choosing a UPS with a wattage rating equal to or greater than the VA rating of the load. Crest factor is the ratio between the instantaneous peak current and the RMS or average current drawn by a load. IT equipment typically exhibits a Crest factor of around 1.4, whereas a PC’s could be 2 or 3. For factors above 1.4, the UPS must be able to deliver the peak current demanded by the load to avoid distortion of its supply voltage. Crest factors are a function of the source AC waveform as well as the load characteristics. Compared with a sinusoidal source, a UPS can reduce the Crest factor of a load such as a PC. The surge factor of a load is the ratio of its startup inrush current to its steady state current demand. For large disk arrays, this can be approximately 1.5, whereas for typical computer systems it is approximately 1.15. UPSs must have sufficient capacity to support the overall surge factor of their driven load.

      Viewing 1 replies (of 1 total)
      • You must be logged in to reply to this topic.