Home » Topics » English riddles » Grounding » Grounding Riddle No.23 – Grounding of auxilary transformer in power plant

Grounding Riddle No.23 – Grounding of auxilary transformer in power plant

  • Creator
    Topic
  • #476
    Guest

      Is it possible to connect such a transformer solidly grounded ( 10/0.4 kv Dyn11 auxilary transformer ) in same grounding as individually high resistance grounded 10kV generator units?
      Is it possible to connect such a transformer solidly grounded ( 10/0.4 kv Dyn11 auxilary transformer ) in same grounding as individually high resistance grounded 10kV generator units? I have understood that solidly grounded auxilary transformers and single phase L-N loads are not possible in high resistance plant and that such loads should be connected as L-L through small transformer.

      Please, can someone advice if this is correct?

    Viewing 1 replies (of 1 total)
    • Author
      Replies
    • #1894
      Hamid

        Service systems rated at 480 V in power plants may be ungrounded, solidly grounded, or resistance grounded. There conditions unique to this service voltage. The possibility transient overvoltage on this system exists as for a higher voltage system. However the insulation of equipment at this voltage level has more inherent per-unit voltage withstand capability. For example, the overpotential test voltage of 2E+1000 for a 460 V motor indicates a withstand strength of 1920 V ac rms, or 4.17 times the motor voltage rating. Comparatively, a 4000 V motor has a withstand strength of 9000 V ac rms, or 2.25 times the voltage rating. It is for this reason and for reasons of service continuity that some system designers will operate a 480 V system ungrounded but will ground a higher voltage system. In spite of the greater percent margin inherent in 480 V insulation, there have been cases of motor failure as a result of arcing grounds at that voltage level. There have also been incidents of voltage transformer damage from neutral instability on grounded 480 V systems. The 120/240 V systems are always solidly grounded. The 480 V systems may be solidly grounded, resistance grounded, or ungrounded. However, even on solidly

      Viewing 1 replies (of 1 total)