How we can calculate the total power transformers capacity which are installed in parallel?
How we can calculate the total power transformers capacity which are installed in parallel?
Viewing 1 replies (of 1 total)
Viewing 1 replies (of 1 total)
- You must be logged in to reply to this topic.

Transformer 1 is thus overloaded by 20 % and transformer 3 by 6 %. Since the individual transformers should not be subjected to overload, the transformers may only assume a partial load such that the impedance voltage of each is uk = 4 %, as in the case with transformer 1. Therefore,
If this output is not sufficient, another 160 kVA transformer with ukr = 4 % shall have to be installed.