Home » Topics » English riddles » High Voltage » High Voltage Riddle No.2 – Transformer insulation failure

High Voltage Riddle No.2 – Transformer insulation failure

  • Creator
    Topic
  • #514
    Hamid

      Consultant team of an industrial power network recommended installation of suitable interconnection between mentioned distributed generation unit and national grid for stability evaluation of industrial electrical system.
      Consultant team of an industrial power network recommended installation of suitable interconnection between mentioned distributed generation unit and national grid for stability evaluation of industrial electrical system. They supply a 132/132 KV,100 MVA transformer with DD0 connection group for establish that interconnection between two 132 KV substations of two independent networks.
      But Installation team didn't know which side of interconnection transformer shall be connected to national grid and they preferred a random selection. After the time that transformer faced a sever insulation failure due to a suddenly voltage fault.
      How can you explain the reason of that serious failure?

    Viewing 1 replies (of 1 total)
    • Author
      Replies
    • #1965
      amir khashayar

        In spite of conformity between two 132 KV windings from rated voltage point of view , it is probable other voltage parameters such as BIL or maximum continuous probable voltage to be different and this point has led to failure. BIL may differ due to method of neutral point grounding , method of connection to connective lines ( cable or overhead line or even busduct).