Home » Topics » English riddles » Wiring and Cabling » Wiring Riddle No.4 – Current rating of bus bar and cable

Wiring Riddle No.4 – Current rating of bus bar and cable

  • Creator
    Topic
  • #564

      For the same sqmm area, the current rating of the bus bar /ayfy cable is different. The current rating of bus bar is lower. why?
      For the same sqmm area, the current rating of the bus bar /ayfy cable is different. The current rating of bus bar is lower. why?

    Viewing 1 replies (of 1 total)
    • Author
      Replies
    • #2133
      Hamid

        It is related to difference between maximum conductor operating temperature of cable and bus bars. The operating temperature of the bus conductors is restricted to 85-90

      Viewing 1 replies (of 1 total)