Can any body tell me what is the permissible value of tangent delta of windings for commissioning of Transformers?
Can any body tell me what is the permissible value of tangent delta of windings for commissioning of Transformers?
Viewing 1 replies (of 1 total)
Viewing 1 replies (of 1 total)
- You must be logged in to reply to this topic.

The overall PF test results of oil-filled power and distribution transformers indicate the insulation condition of the solid windings, oil, barriers, bushings, etc. The overall PF value for individual windings-to-ground and inter windings insulation of modern oil-filled transformers should be 0.5% or less, corrected to 20