Home » Topics » English riddles » Transformer » Transformer Riddle No.55 – Optimum value of tangent delta

Transformer Riddle No.55 – Optimum value of tangent delta

  • Creator
    Topic
  • #605
    Sreelatha Gajjala

      Can any body tell me what is the permissible value of tangent delta of windings for commissioning of Transformers?
      Can any body tell me what is the permissible value of tangent delta of windings for commissioning of Transformers?

    Viewing 1 replies (of 1 total)
    • Author
      Replies
    • #2251
      Hamid

        Power-factor or dissipation factor ( tangent of the loss angle) testing of insulating oil shall performe in accordance with American Society for Testing and Materials (ASTM) D 924, Standard Test Method for Dissipation Factor (or Power Factor) and Relative Permittivity (Dielectric Constant) of Electrical Insulating Liquids as below: The overall PF test results of oil-filled power and distribution transformers indicate the insulation condition of the solid windings, oil, barriers, bushings, etc. The overall PF value for individual windings-to-ground and inter windings insulation of modern oil-filled transformers should be 0.5% or less, corrected to 20

      Viewing 1 replies (of 1 total)
      • You must be logged in to reply to this topic.