Electrical Test Riddle No.2 – Generator loss tangent test

  • Creator
    Topic
  • #642
    Hamid

      Please find the final test report of an industrial generator which submitted by an international famous manufacturer for a new production as following.
      Please find the final test report of an industrial generator which submitted by an international famous manufacturer for a new production as following. Why determination of insulation capacitance or loss tangent in %20Un is more important than rated voltage?
      What is your opinion?

    Viewing 1 replies (of 1 total)
    • Author
      Replies
    • #2306
      Glavizh

        Something has been mistaken . It is not Tan Delta at 20% of rated voltage . It is the difference of Tan Delta at steps of 10% or 20% . Generators manufacturers use insulating paints in end winding of stator (normal insulation is not possible for end winding) . The performance of insulating paint is not linear versus voltage increasing and nonlinear performance should be verified.