Transformer Riddle No.66 – Impedance of a transformer

  • Creator
    Topic
  • #733
    Sreelatha

      In order to increase the impedance to tertiary winding in a single phase autotransformer tertiary winding is placed on outer limb of a 3 limbed single phase or a 4 limbed single phase configuration….
      In order to increase the impedance to tertiary winding in a single phase autotransformer tertiary winding is placed on outer limb of a 3 limbed single phase or a 4 limbed single phase configuration.

      Regulating winding is also placed on outer limb to reduce transfer surges to tapping winding from reliability point of view. This arrangement requires a compensating winding on a main limb feeding the regulating winding on outer limb so that distribution of 50% flux to outer limb is ensured.

      I shall be thankful if somebody can help me to decide

      i) current rating of compensating winding

      ii) calculate % impedance from HV to tertiary and LV to tertiary by classical formula.

      Regards
      Sreelatha

    Viewing 2 replies - 1 through 2 (of 2 total)
    • Author
      Replies
    • #2547
      Hamid

        1-For the purpose of illustration it is possible to put some typical values on the booster arrangement of Figure below. This might be required to provide a phase shifting capability of 18

        #2549
        Sreelatha

          Dear Sir, Thank you very much for your reply. You have given the impedance calculation for normal arrangement. But I wanted the calculation of impedance between windings placed on different limbs. Kindly help me in this regard. Thanks & Regards Sreelatha

        Viewing 2 replies - 1 through 2 (of 2 total)