      Rating of a furnace transformer in delta primary is ok but if primary in star transformer kva rating is less than of the rated capacity why?
      Rating of a furnace transformer in delta primary is ok but if primary in star transformer kva rating is less than of the rated capacity why?

    Viewing 1 replies (of 1 total)
    • Author
      Replies
    • #2778
      Hamid

        Rated KVA (S) of transformers is: S = ?3 V.I Which V and I are winding transformer voltage and current rated capacity respectively. When you change the primary connection from delta to star, you loss a part of transformer capacity, because you cannot increase transformer current from its rating (I) while you apply 1/?3 V (rated voltage) to primary winding.