Home » Topics » English riddles » Protection » Protection Riddle No.88 – High impedance protection CT Mis-match

Protection Riddle No.88 – High impedance protection CT Mis-match

  • Creator
    Topic
  • #928
    Addis

      For high impedance restricted earth fault protection it is known the neutral CT ratio of the power transformer must much with the line CT, But during Test and commisining i have got a problem, …
      For high impedance restricted earth fault protection it is known the neutral CT ratio of the power transformer must much with the line CT, But during Test and commisining i have got a problem, as the neutral CT of Power transformer has CT ratio 100/1A but the line CT has 75-150/1/1/1A CT? how can i resolve this problem?

    Viewing 3 replies - 1 through 3 (of 3 total)
    • Author
      Replies
    • #2975
      Hamid

        There isn’t any recommended solution; you must use similar line and neutral CT or low impedance (biased type) differential relay. Of course using of interposing CT for ratio matching can be an urgent/temporary solution, but other CTs mismatching such as internal resistance and magnetizing current can be caused protection instability against out of zone earth fault and generally it is not recommended. A number of design considerations must be taken into consideration when designing a high-impedance REF scheme. The most important considerations are described here: – The ratio of the phase and neutral CTs must always be the same. – In general, the CTs should have the same saturation characteristics. – The kneepoint voltage must be higher than the stabilization voltage for external faults. – The voltage across the relay and CTs (all in parallel) should be kept at safe levels while still being sufficiently high to allow operation of the relay when required. The magnetizing current of the CTs depends on the voltage across it, but too high a voltage results in higher magnetizing current that leads to a less sensitive scheme. – In most cases, a metal oxide varistor (MOV) or surge arrestor is connected across the parallel connection of the CTs and relay to clamp the voltage to a safe limit, without affecting relay operation. The MOV protects the relay against high voltages developed during inzone faults. Sufficient current still flows through the relay to ensure operation.

        #2985
        Addis

          Currently i don’t have chance to make the CTs ratio the same, else the solution is to use “low impedance (biased type) differential relay” and my question is how can i change the high impedance restricted earth fault relay to low impedance (biased type) differential relay what is the idea behind? and is it permanent solution I mean how much the power transformer is protected by doing so? can you give me brief things on the difference and similarity of the two protections? thanks inadvance

          #2986
          Hamid

            The high-impedance REF relay is normally a currentoperated relay with a resistor in series that provides stabilization. Generally, it may be one of two different types. The first type has internal resistors and has a voltage setting. In this type, the resistors are effectively switched in and out to change the setting and therefore the value of the stabilizing voltage. The second type has an external variable resistor where the setting is calculated in ohms and applied by changing the resistance of the variable resistor. Any mismatch in CT ratio will result in spill current, part of which will flow through the relay. Spill current cannot be related to current that flows on the primary side and flows on the secondary side. It may, therefore, cause the flow of

          Viewing 3 replies - 1 through 3 (of 3 total)